I had sent a different project from gmail. I had the same problem before. When the cross section between 3-4 axis is taken, the program throws.. the project is attached
The problem will be fixed in 6.53 update. Good work..."quiet_2121":2a1mxzk5" said:The program crashes when the section between 3-4 axis is taken..the project is attached
thank you."YasinTezel":97e30r99" said:I drew the slab edge on the E axis, defined the slab gap from the continuous foundations you defined, hollowed out the continuous foundations, and defined another raft foundation at low elevation, Levels, continuous foundation and raft You can adjust the foundation thicknesses according to your project."coskun3561":97e30r99" said:I stated that I don't want to do it with the tile gap. That way I can already do it. my purpose is to close the edges of the space with beams. There must be a slab edge on the E axis, it may have been erased.
Actually, you already answered your question in the question you asked.. Negative stress occurs on the raft and the program does not warn you when you cancel that control. Examine the results of the ground stress in the report and from the 3D frame. Look at the magnitude of the negative stress and the areas where it is effective. If you add the project, we can find it in a clearer comment. Good work..."coskun3561":gaapjhxd" said:I made a raft foundation in my 2-storey single flat project. When I tick the negative ground stress control, I can't save it on the raft at all. But when it is unchecked, even 30 cm raft saves...
If you change the direction of the S68 column and make a matte raft solution, negative stress - It decreases down to 0.5 t/m2 (g+q-Ey2 loading.) I think this stress is at a negligible level... If you want to remove the negative stress, you need to review the carrier system. It basically comes out larger than q and so the combination becomes negative. I saw an error in your data. You can also see the error in the geometry check. The beam on the S axis (K609) and the beam K591 do not match each other. The same is true on the other floor. You fix them. Good work ..."coskun3561":f9n1m5sn" said:negative stress error remains when I narrow the foundation. I kept the foundation wider so that the further I keep it away from the building, the better.
has been overlooked, I think we are more careless and make more mistakes in small projects. Thank you. good work to you too"HakanŞahin":3fgqwjqs" said:If you change the direction of the S68 column and make a matte raft solution, the negative stress decreases to -0.5 t/m2 (g+q-Ey2 loading). I think this stress is at a negligible level... If you want to remove negative stress, you need to review the carrier system. Since the number of floors is low, the earthquake loading is greater than g+q in negative loading; and thus the combination becomes negative. I saw an error in your data. You can also see the error in the geometry check. The beam on the S axis (K609) and the beam K591 do not match. The same is true for the other floor. You fix them. Good work..."coskun3561":3fgqwjqs" said:negative stress error remains when I narrow the foundation. I also kept the foundation wider so that the further I keep it away from the building, the better.
There is no problem with the connection in the S27 column. Only the S25, S27 and S24 columns are not on the same axis, so the bases do not overlap in line arrangement. If you get the continuous foundation report, you can see that the S27 column is taken into account in the support of the TK77 and TK71 foundations. In addition to your question, I draw your attention to the continuous foundation connected to the P3 panel. Insert the TK58 foundation sitting on the P3 panel, holding both ends of the panel. In short, the 1st end of the P3 entering the TK58 Enter by clicking , P3 end 2 and S18. Catch Tk60 also from P3 end 2. Good work..."musti776":3iac2hyz" said:I couldn't do the basic combination of the s27 column, thank you very much if you can help.