Opinions questions about using ideCAD Static 7

Hello, Stirrups come out with 15 cm intervals in the wrapping area in the vertical expansion of the column. What could be the reason for this? My project is back. I noticed something like this in another project. Is this an error? Also, as you go up to the upper floors, the column reinforcements increase. Thanks for your answer.
 
I found the answer to my question. There is also the statement dbybhy 2007 that it cannot be less than 15 cm in the besieged junction areas. So, is it normal to increase the vertical reinforcement of the column as you go up to the upper floors?
 
"windtalker":3pwfimlk" said:
Hello, Stirrups come out with 15 cm intervals in the collapsing zone in the vertical expansion of the column. What could be the reason? My project is back. I noticed that there is a similar situation in another project. Is this a mistake? Also Column reinforcements increase as you go up to the upper floors. Thanks for your answer.
Hello, If the column was found to be "enclosed" in the column-beam shear safety check, the reinforcement spacing in the junction area may be 15 cm. In the picture you show as an example, the column looks like a "enclosed column". If so, the spacing chosen by the program is not incorrect. If the column is enclosed, the spacing at the junction<=150 mm. If the column is not enclosed, the spacing is <=100 mm at the junction.
 
"windtalker":80dzq7ej" said:
I found the answer to my question. The statement that it cannot be less than 15 cm in encircled joints is available in dbybhy 2007. Is it normal for the vertical reinforcement of the column to increase as you go up to the upper floors?
It may be due to the difference in Moment/Normal Force ratio in the upper floors. When there is excess reinforcement on the upper floor, the program connects the anchor reinforcement and the reinforcements. If you do not prefer it this way, you can equalize the reinforcements from the top floor to the bottom floor in the column reinforced concrete dialog. Good work.
 
Thanks for your quick answer. I came to a conclusion about the torque/normal force ratio. Since the axial load is high on the lower floors, the moment carrying capacity also increases at this rate. Therefore, no extra equipment is needed. As you go up to the upper floors, if the moment is high (which in my project I increased the loads due to the roof piece), the main reinforcement increases to carry this moment. Since the axial load is also low, it is not possible to contribute to the carrying capacity. So, can excess reinforcement on the upper floors have a negative effect on the lower floors? Could a more ductile behavior occur in the lower floors?
 
Hello, In the attached project, the loads on the beam are quite high and I am having trouble with shear safety. Increasing the beam size is more of a problem than a solution. I guess it doesn't help much if I increase the size of the colon. Concrete grade C50 is not very effective to enlarge more, even that is quite a lot. I would be glad if you help. Good work. download link:
You do not have permission to view link Log in or register now.
 
"windtalker":k3orak5p" said:
Hi, In the attached project, the loads on the beam are quite high and I have a problem shear safety. Increasing the beam size is more of a problem than the solution. Increasing the column dimensions does not help much I think it is not very effective to enlarge the concrete quality C50 more, which is quite a lot. I would appreciate your help. Good work. Download link:
You do not have permission to view link Log in or register now.
 
The building was designed as a basement floor and was divided into 3 areas with 2 dilatations. This is the middle part. There are steel rack systems on this structure, and the loads on the rack legs are 14 tons - the loads defined on the beams - I defined the tower as a basement curtain in order to remove the phrase "There is a curtain in the system" and enter the R coefficient of 7. At the same time, small loads from the steel structure will be transferred to those curtains. Based on what I said, should I still do what you say? The project has not been a concept design application before, so I think I will tire you out a bit. I need your help as a detailed study is required. Thank you for your answer.
 
"windtalker":1kr4atxe" said:
The building was designed as a basement floor and divided into 3 areas with 2 dilatations. This is the part in the middle. There are steel shelf systems on this structure and the loads on the shelf legs are 14 tons - the loads defined on the beams - the curtain in the system I defined the tower as a basement curtain in order to remove the var expression and enter the R coefficient of 7. At the same time, small loads from the steel structure will be transferred to those curtains. If we look at what I said, should I do what you said again? The project is a concept design, there is no application before, so I think I will tire you a little. A detailed study Thank you for your answer.
If the dilation is a separate structure from the whole structure, it would be usual for you to consider the situations that change according to the selected system, such as the R coefficient, rigid basement, and the number of modes. ; helps your questions about "data entry in the program" or "solving the problems you have in the program" We will be pleased. Good work
 
Good afternoon, After creating the Layouts, I want to put a 3D view of the structure at the end. Is this possible? No need to write anything on it. Just an isometric view (not necessarily perspective). Thanks.
 
"yagmurcankocak":18oqwdut" said:
Good afternoon, After creating the layouts, I want to put a 3D view of the building at the end. I wonder if this is possible? It doesn't need to have anything written on it. Just an isometric view (not necessarily a perspective) Thanks.
Hello, make a vector drawing of the 3D image. Then you can copy/paste it to the end of the sheet. Right click on the perspective image/Create Vector Drawing.
 
Are there special design loads for mosque minarets? Is the minaret account made with idecad? I'm asking for help from my friends...
 
Hello, Is there any problem in terms of data entry in the attached file? Are there any problems in terms of loadings on beams, column loadings, surcharge and soil thrust loads on walls? There is a steel shelf system (graveyard system shelf) on the reinforced concrete structure and the loads on the beams come from these shelf legs. This building, which was designed as a basement, remains underground. The other day, you suggested that I enter the rigid floor number of the 2nd part of the building as -2. I applied the same in this structure and there is no problem in terms of cutting safety. Is this a correct approach? Although I did not choose the design option without pillars on the beams, the program designs without piles. What could be the reason for this? Thanks.
You do not have permission to view link Log in or register now.
 
The attached project is the 2nd part of the above project. I applied the analysis settings you specified to this project. Up to 25 mods, the analysis ends with the error 'Insufficient number of mods taken into account dynamically'. When I switch to 50 mode, the program closes after modal analysis. I think there is a problem with the connection of the building elements, but I could not find it. In the report, although Ve+ Ve- values are greater than Vr values in some beams, no errors are shown in red. When I solved it as Rijt botrum the error was shown in red in those beams. Thanks. Project download link:
You do not have permission to view link Log in or register now.
 
4 parts of the project are attached and this part will be designed as a raft. How can we design the calculation axles for such a raft? In the same way, there are 2 more parts. How should I set the analysis settings in these parts? I'm considering a semi-rigid diaphragm solution. What should be taken as the R coefficient? As I mentioned before, there is a steel shelf system on this part. Should I take the coefficient of the steel part as the R coefficient or should I consider it as a reinforced concrete raft? I took the loads from the superstructure as live loads, maybe that's why I can take R for reinforced concrete. I transferred the loads from the superstructure from the bottom of the small reinforced concrete columns to the raft, is this approach correct? Thanks. Download link:
You do not have permission to view link Log in or register now.
 
"windtalker":jkwf7n6f" said:
Hi, Is there any problem in terms of data entry in the attached file. Is there any problem in terms of loadings on beams, column loadings, surcharge and soil thrust loads on curtains?
Hello, beams and columns and The directions of the loads given to the panels seem correct.
The program is designing without pillars even though I did not choose the pillarless design option on the beams. What could be the reason for this? Thank you. (Minimum pile lower remaining and min pile lower remaining L/2 parameters) If pile breaking conditions are not met, pile will not break. Other cases; *Different names have been given to the parts of the beams divided between columns in the project. This is not appropriate for reinforced concrete. For example, S8-S17 columns The beam between the two is named K7-K8. It is utilitarian to just call this beam K7 or K8. it would be appropriate. Thus, in this and similar situation beams, the clean opening will increase and the pile will also break. *Analysis method selected semi-rigid diaphragm. A support arrangement was not made on the stairs according to the solution conditions together with the structure. Good work
 
"windtalker":1ct5h4u8" said:
The attached project is the 2nd part of the above project. I applied the analysis settings you specified to this project. The analysis ends with the error 'The number of modes included in the dynamical calculation is insufficient' until 25 modes. When I switch to 50 modes, the program ends after the modal analysis It closes. I think there is a problem in the connection of the building elements, but I couldn't find it. Also, in the report, even though the Ve+ Ve- values are greater than the Vr values in some beams, the error is not shown in red. When I solved it as Rijt botrum, the error was shown in red in those beams. http://www.dosya.tc/server2/OzkokL/IRONMOUNTAIN.rar.html[/url]
The height of the stairs is not compatible with the basement floor. Therefore, the upper edge of the stairs is not connected to the beam. The height of the lower level is entered 2.35 meters to the floor. 45 mods are sufficient when harmonized with. Moreover, even if the number of mods is 60, the analysis is completed. The value of Ve, which is smaller than the calculation made according to Ve(R=2), is compared with Vr.
 
Should only beams between columns be considered continuous? In this case, I think I will have to re-enter the beam loadings. The support regions at beam intersections (the parts shown in green in 3b) are not included in the beam length. In the middle of these beams, which I always accept, support zones will be formed. How will I provide data entry on the beams in this drum? thanks.
 
"windtalker":3i333q5g" said:
Should only beams between columns be considered continuous? In that case, I guess I'll have to re-enter the beam loadings. At beam intersections, the support regions (the parts shown in green in 3b) are not included in the beam length. This is what I've consistently accepted There will be support zones in the middle of the beams. How will I provide data entry on the beams in this drum? Thank you.
The names of the beams can be decided according to the moment diagram. For example, in the attached picture, the moment diagram of the beam on 2 axis is formed in two separate sections, K1 and K2, since negative moment occurs in the middle of the span. It would be appropriate to give a name. The places shown in green in the 3d frame are also rigid arms (beam-beam intersections).
 
Hello, There is a problem with the computer shutting down in the section below. There is an incorrect join that I can't catch. Is there an easy way to view these errors? Thanks