Hello Project; The ratio of the total shear force total to the total floor shear force gives a warning of greater than 0.75. How can a solution be made? Thanks.
 
"ertub_23":16rfwboa" said:
Hello In the project, the ratio of the total shear strength of the total floor area to the total floor shear force gives the warning that it is greater than 0.75. How can it be solved?
Hello. You need to enter the value of 10-4alfaS calculated in the X and Y directions, which you can see in the R Coefficient report
 
Is there a need to place columns on the headboards on the curtains? They do not give the head reinforcement drawing in the drawings.
 
"ertub_23":26cil4pv" said:
Is there a need to place columns on the headers on the curtains? It does not give the head reinforcement drawing in the drawings.
No, there is no need. If the curtain header regions are not created, the conditions of DY 3.6.2 are not met or there is a problem in your data entry.
 
"ertub_23":kiy32u0z" said:
HEAD COLUMN DRAWING ON CURTAINS DOESN'T DRAW DRAWING HEADING COLUMNS CAN YOU REVIEW THE PROJECT.
"YasinTezel":kiy32u0z" said:
the conditions of DY 3.6.2 are not met if headline regions are not created
hw/lw Since it is <2, the title region is not created in the curtains. However, if you want to create a header area on your curtains, it is also possible to define a header area in the panel settings "rebar" tab.
 