lack of reinforcement and shear force

hakanburak

New Member
I couldn't solve the problem of lack of reinforcement and shear force, I tried the short edge size increase, I'm waiting for your opinions, thanks
 
Hello, If you remove the sign in the reinforcement fixing column of the beam number K023 on the ground floor in the beam reinforced concrete dialog for the situation you specified, and repeat the analysis, the problem is solved. Other issues identified in your project; -There is a vertical continuity problem between the column number S64 on the ground floor and the column number S57 on the basement floor (You can see this in the Geometry Control dialog). If the S57 column is deleted and the S64 is copied from the ground floor, the problem is fixed. Instead of defining a basement floor with a height of -80 cm, it would be more appropriate to make the height of the ground floor 430 cm and define the basement curtains by giving an upper level of -350 cm in this floor. You can find more detailed information about the definition of basement curtain from the link below. Detailed information about the definition of the basement curtain:
You do not have permission to view link Log in or register now.
-The left end of the foundation of TK002 is not connected to the column number S62 because it is finished on the D axis . -The left end of the foundation number TK021 is not connected to the foundation number TK008. If you re-enter the TK021 basis by activating the divide by intersection command, the problem will be fixed. The definition of the base TK020 entered under -S57 appears to be incorrect. Instead of defining this foundation, you can increase the widths of the foundations TK013 and TK016 to cover S57.
 