"geylanikiymet":35k3hfbt" said:
Good day, I created a system taking into account your suggestions, but I could not make the sloping roof on the roof, it constantly gives errors, incorrect beam intersection, vertical discontinuities, etc. Can you review and help about the roof as of now? Many thanks in advance
Hello, Our general recommendations and suggestions for data entry are as follows; -4. The elevations of the columns S03 and S04 on the 3rd floor are not compatible with the columns on the 3rd floor. The elevation of the 3rd floor S021 flooring is not compatible with the curved beams. The slab edge may be scratched so that the slab is not attached to the joists. The elevation of the slab S020 at +135 level on the -3rd floor is not compatible with P01 and P02. The upper elevation of P01 and P02 on the 3rd floor is +135 cm, and the elevation on the 4th floor is +135 cm. (S20 slab may not be operated as a rigid diaphragm.) -3. The slope of the k03 beam of the 3rd floor should be arranged so that the elevation is compatible with the slab. - It is appropriate to analyze with semi-rigid diaphragm method for connecting sloping floors to columns and each other. -It would be appropriate to model the curtains as shells. - If the column header defined for the S10 column in the basement floor is to be applied in architectural plan mode and on site, it must be defined according to the conditions specified in TS 500. You can download the sample data from the link.
Good work