Composite slab results...?
ammer
Dear All, Marhaba...
How can we get the result of the composite slab? I mean, we can get the results of the composite beams easily, but what about the composite slab, regarding deflection or the adequacy of the metal sheets?...Best Regards
In addition to my previous question, is there any way to predict the quantity of the metal sheets on the concrete for the composite slab ??
thanks
Hi Ammer;
We design composite beam with the concrete slab by this means we calculate neutral axis the total slab(steel,deck and concrete) and PCS. If PCS is over the % 100, this means concrete slab is not working enough and you should increase the capacity of concrete. We also check the deflection, which you can see at composite beam design, by using concrete and steel deflection. ın summary, the deflection of the composite beam is total deflection and no further requirement for another deflection control.
In composite slab menu you can see materials for concrete and steel, the material of steel is for metal sheet not the composite beam. The metal sheet role is formwork so it's not necessary to control the capacity of bearing.
All of these; you can see the details like capacity control, PCS, deflection and other regulation controls at composite beam design menu and composite beam reports.
Best Regards.
Dear Ammer,
As explained you can perform only composite beam design. "Composite slab design" is an issue about the metal deck, its form, concrete, reinforcement and support conditions but mostly metal deck, its form and bonding to the concrete. Thus, this issue concerns the metal deck manufacturer and you should ask this design calculations to them. They are responsible to make tests or calculations for their metal deck products to be used in composite construction and share the results (for different support, load, concrete thickness etc. conditions) with the designers.
For example, please check:
Best regards,
Tolga Aydöner
