Hello Mr. Ahmet, TS 498 or TS EN 1991-1-4:2005 and DBYBHY 2007 resources are sufficient for the subjects you have mentioned. When calculating the wind load, first of all, in TS 498 Table 5, totem signage max. q according to its height, by determining the wind suction pressure (if a part of the sign area falls below 8 meters, it will be safe for you to take the q value of 80kg/m² for the whole sign) and for the C coefficient, you should choose the value 1.6 by "accepting" option a of 2.1 item in Table 6 will be appropriate. However, since there is no special C coefficient explanation for this type of structures in TS 498, it would be healthier to calculate the wind with this standard, taking into account the specific explanations in the article 7.4.3 of TS EN 1991-1-4:2005 for the relevant coefficient. Taking the building importance coefficient as "1.0" from DBYBHY 2007 Table 2.3, and since the building is not a building type, for the structural system behavior coefficient R, Article 2.12 is given in Table 2.8 as "Inverted pendulum type structures whose mass is stacked on the top and carried by a single independent vertical carrier element". You can consider the value "2" given in the title. I wish you good work. Best regards, Tolga Aydoner