The program gives an error when the beams are given wall load.

"mhmt_ali":3ew9rb9q" said:
An error occurs when giving 19 cm wall load to ground floor beams K1,14,13,09,10,11,12,21,22,04 and 17. Can you help with this. [url =https://www.file.tc/server25/i439k1/G-H_BLOK3.ide10.html]https://www.file.tc/server25/i439k1/G- ... ide10.html[/url][ /quote] If by error you mean B1 (Weak floor) irregularity; -B1 (Weak Floor) Irregularity occurs when the effective shearing area on a floor is less than the value specified in the regulation when compared to an upper floor (TBDY 2018 item 3.6.2.3) Variables in the shear area walls, columns and walls.The wall loads entered in the beam settings are taken into account as the effective shearing area in the control of B1(Weak Floor) Irregularity.You can check the frequently asked questions link, item 35.
You do not have permission to view link Log in or register now.
Notes: -If there are walls on the basement perimeter curtains, you can define these walls in the project by using the wall command. Curtains defined as n are not included in the floor effective shear area in B1 irregularity control. In cases where the curtains should be marked as basement, you can add the relevant curtain fields to the +Agx, +Agy columns in the Analysis / Floor parameters / Irregularities tab. -Structural system behavior coefficients (Rx, RY) and strength excess coefficients (DX, DY) have been entered in the Analysis Settings. (In the TBDY 2018 wizard, select the carrier system type A11 in the X direction, A15 in the Y direction and use the values from this selection.)
 