I am using idecad 6 version, even though I throw a reinforcement curtain, it shows as a collapse risk in the system. Am I defining the reinforcement screen wrong? I will be glad if you help.
 
Hello, Corrosion and insufficient reinforcement clamping or overlapping length multipliers on the curtains are left at 0 and 0.4, respectively. Take these values as 1. If necessary, enter a value between 0 and 1 depending on your system. (item 7.2.3 for corrosion and 7.4.14 for insufficient reinforcement clamping or overlapping length) When performing performance analysis, take the structural importance factor as 1, not 1.5. (item 7.4.2) Good work...
 