stapling security is not provided

kübra

New Member
Hello, I tried a lot, but the stapling security is not provided and I could not solve the curtain cut security error. What can I do?
 
Mr. Kübra My suggestion to your project 1- Your ground safety is very low. D group may enter the ground. If there is group D, you cannot enlarge 50%. 2- Console floors connected to the basement curtains are disrupting the system. Delete DZ01-02 and analyze. If you add it later in the drawing. When the tiles are deleted and analyzed, there is no stapling problem. 3- You have given the curtains that you need to give as basement curtains as normal floor curtains. 4- COLUMN-CURTAIN-BEAM DEFECT LOCATIONS As you can see, you can remove the basement curtains inside the building. When these curtains are removed, make the narrow side of the column at least 35 cm, since the length of the columns in the front and back are doubled. On the upper floors, do not make the narrow side of the column less than 30 cm thick. 5- the bracing is wrong. Beam support KIRIS JOINT as seen. This error exists on every floor and should be fixed. 6- There is no continuation of the beam at the shear-beam junction where BREAK JOINING is seen. 7- Most importantly, your curtains are insufficient in both directions. Better put additional curtains in both directions. 8- If the KZ5 opening is seen more than 3m, increase its height if necessary. 9- Check and enter the stair and wall loads. Take it easy Unver ÖZCAN
 