hello, the attached visual is the page that shows the strong column control of the project report. Here, the last column titled "result and explanation" says Mrkol>1.2Mrkiriş, but it seems that my columns did not meet this requirement. It says top floor object as description. Couldn't I provide strong column control here, why didn't the program give a warning after the analysis, I guess strong column control was not done on floors that did not continue. my build is single floor. I wonder if this is why the top floor object is writing, so is there a problem or not?
 
Hello, Columns of single-storey buildings or top-floor columns of multi-storey structures are exempt from totalMrkol>1.2*TotalMrbeam control. The program therefore did not issue a warning. See TDY 2007 item 3.3.5.4b.
 