If you are going to do a performance analysis, I don't know how accurate it is to increase the loads in order to stay on the safe side. The main thing here is to model the building as close to reality as possible. That's why I suggest you rethink the load issue. In this context, having a project or having a building subject to inspection does not require you to have a "comprehensive" level of knowledge. You should gather information from the structure with adequate inspection. You must perform the beam and column reinforcements with destructive stripping and x-ray equipment. That's how you can tell if your project is being followed. In particular, it is not possible to see stirrups, stirrup hooks and corrosion conditions without stripping the reinforcement. You can see where and which element will be strengthened from the column, shear and beam performance analysis results. Here, under each element, it is written which type of damage it is exposed to. Based on this, you should decide whether you will strengthen that element or add an additional reinforcement curtain that will reduce the loads on that element. If you examine the TDY section 7.7 and the table in which it is found in the reports, it will guide you.