performance analysis

Get a performance analysis report. In this report, consider the topic of building performance according to TDY 7.7. life safety performance related to advanced damage and collapse elements in each earthquake direction (+EX, +EY, -EX, -EY) Examine the ones that do not comply with the section 7.7.3[/u] of the regulation for level. The number of elements for each floor in the advanced damage and collapse zone is written here. The names of the elements that need to be strengthened are written in the continuation of this report. When you look at the rest of the report, for example, in the Column Performance Analysis results, information about each column is given one by one. Here, under the name of the column, it is written in which damage area it is located. These can also give you an idea. For example, in your system, S209-S109-SZ09-SB109 columns, S112-SZ12 columns, S115-SZ15 columns and SZ11 column are in the collapse zone. It is expected that the curtains will be strengthened in your system. Particularly in the +EX, +EY directions, the columns in some floors seem to be in the collapse zone. Although the curtains are expected to get stronger, you can add curtains to the system at other points to take the load of the curtains in question. You can also strengthen the columns in the collapse zone. Depending on the flexibility of the architecture, you can make these experiments.
 