Nd and Nk problem

mhmt_ali

New Member
In the project I just started, although the column sizes are sufficient, the Nd Nk warning shown in the picture is given during the reporting phase. Can you help me to fix this?
 
Hi, according to TS500, the total column axial design loads should not be greater than 0.45 times the total column critical loads. The standard says that if this condition is not met, you need to increase the column dimensions. I suggest you to review the 7.6.2.5 section of the TS500 on the subject.
 