I get the error that the slab thickness does not meet the required condition.

201968

New Member
In the attached project, I get the error that the slab thickness does not meet the required condition. I changed the reinforcement type from the reinforced concrete calculation axle edit section, but it did not save. Is there any way I can fix this error in a different way? (Slab thickness 20 cm and without adding beams) Waiting for your suggestions. I would be glad if you help. Thanks good work
 
Re: FLOOR THICKNESS
"201968":1r5yyday" said:
I am getting the error that the slab thickness does not meet the required condition in the attached project. I changed the reinforcement type in the reinforced concrete calculation axis edit section, but it did not save. I have the opportunity to fix this error in a different way. (Slab thickness is 20 cm and without adding beams) I am waiting for your suggestions. I would appreciate your help. Thank you. Good work
Floor thickness (as it is written in the geometry control) should not be less than the value in TS500 11.4.2. This formula and Accordingly, the minimum floor thickness should be hf= 23.61 ~ 24 cm.
 