I'm getting double reinforcement required error

referansstatik

New Member
Why am I getting a double reinforcement error on the floors, where is my error? When I say use mesh reinforcement, the line clears but I didn't know how to switch to double reinforcement..
You do not have permission to view link Log in or register now.
 
Re: DOUBLE REINFORCEMENT REQUIRED ERROR ..
"referansstatic":3oqxv240" said:
Why do I get a double reinforcement error on floors? .
You do not have permission to view link Log in or register now.
The double reinforcement (DD) warning is due to the analysis performed according to the "Consider in-plane forces in the slab design" option in the Semi-rigid diaphragm method in the Analysis Settings. Your problem can be solved by arranging the slab reinforcements as top + bottom flat reinforcement with the "Reinforced Concrete Calculation Axis Edit" command. Project notes: -It is seen that there is no perimeter curtain on the basement floor. The floor should not be considered rigid. -The Tile type is incorrectly selected in the TBDY 2018 Wizard. Also, the carrier system type is not selected in the Y direction. -It would be appropriate to analyze the dilations in separate project files. Good work -
 