Excess equipment coming out

Re: extra reinforcement - In the project you added, the slab type was incorrectly selected in the TBDY wizard. It is necessary to choose one-way gear flooring. In this case, the building height class requirement given for unidirectional gear floors in TBDY 2018 Table 4.1 is not met. The ductility level must be mixed and the curtain rollover control condition must be met.
 
It is necessary to choose one-way gear flooring. But selection is not allowed. If the ductility level is mixed, the reinforcements give an absurd surplus.
 
"bagcihan":39dr5ynx" said:
Single direction threaded slab must be selected. But selection is not allowed. If mixed ductility level is selected, the reinforcements give absurdly excess.
In your project, Building Height Class BYS=5. For unidirectional threaded slabs It does not meet the allowed DMS condition. I added Table 4.1 in my previous message. The mixed solution conditions for the ductile level are also not met. In order to solve the mixed Ductility Level mixed system, the condition TotalMdev>=0.75*Mo specified in TBDY 2018 item 4.3.4.6 must be met.
 
Is it okay to leave it like this, and I get an error in round columns, I don't know if it is an error in the calculation of the program or in the design
 
"bagcihan":2yry4lbz" said:
is it right to leave it like this, I also get an error in round columns, I don't know if it is an error in the calculation of the program or in the design
If a solution is made in this way, the conditions specified in TBDY 2018 for unidirectional gear flooring You can change the flooring system.
 