Dear colleagues, Collapsed under vertical loads, the attached report of Zümrüt apt. Many of you know. I did a detailed investigation and reached the following results. I ignored the manufacturing errors and it is available in the report (etabs) that nothing extra was done apart from the one in the project (including the GROUND report). When the formwork plan is examined, 1) The discontinuity of the system, in which the console overhangs are not connected with beams, could not be ensured. However, although this forces the system, I think there is no reason for it to collapse only under vertical loads. It poses a great danger in case of earthquake. 2) There are excessive studs in the system, the studs are arranged close to the column to disrupt the frame system and this will cause trouble in load transfer. 3) Most of the column directions are strong in the y direction, which again poses a great danger in the event of an earthquake. 4) The difference between RM and KM is mentioned in the report, which creates the A1 irregularity. However, there is a sanction in the regulation that only affects the calculation method related to the A1 irregularity. *Result; In these project flaws that I have seen (only by looking at the mold plan), it says to create your frame exactly in the first articles of the regulation, but shouldn't there be a control mechanism about it? *Do you think these points are enough for the structure to collapse only under vertical loads? Or did this build collapse for some other reason? *The report was analyzed according to etabs and it was seen that the size of the columns should be larger than necessary. However, are there any differences when the projects made with idecad sta4cad,probina are compared with foreign sourced software such as etabs sap? NOTE: My aim is to prevent and prevent wrongdoing unknowingly, and to show that 92 lives can be costed to those who do wrong on purpose. Waiting for your valuable comments, good work, best regards