emergency aid

hlyrkn

New Member
I made a large span project solution. sections saved, but I need a better solution suggestion. I have attached the project, I would be very happy if you examine it and give new ideas.
 
- When you check the geometry, you see something. You must exceed the curtain width clause. Your floor height is 4.00 m. Accordingly, your width should be at least 27 cm. If I were you, I would make at least 30 and make the curtain size 30/210 cm (1/7). thus the beam width is also increased by at least 30 cm. The manufacture of beams of such height (25/80) may not be smooth. - If it were me, I would make the beams like 70/70 with multiple stirrups. - It was a good idea to choose the high concrete quality. - Why didn't you consider cassette flooring in such a large flooring? - I think you know the reason why the live load is 200 in such a wide span. I think your loads are worth checking out. - You said that the sections saved, but I calculated, there are objects that did not save. Your floors have a deflection problem. The dimensions of the slabs in this opening should not be this size anyway. Your rib heights are insufficient. - I'm not counting your raft flooring. In short, that's all I can say.
 
CURTAINS WAS SELECTED TO BE LEFT HIDDEN ON THE WALLS. I SAID TO FLOOR A CASSETTE, BUT IT IS NOT WANTED, SO I HAVE TO MAKE RIBBONS. I CAN MAKE A DOUBLE STRIKE TO THE BEAMERS. YOU ARE TRUE. SO HOW DOES THE SYSTEM CANNOT SOLVE DIFFERENT TO YOU OUTSIDE THE CASSETTE?
 