I also agree with Nedim. These are my personal opinions, but I am writing to give you an idea. Both basement floors do not comply with the definition of rigid basement in the regulation. The rigid basement floor number should be -3. Even if it is a basement curtain, the placement of basement curtains is not symmetrical in terms of rigidity distribution. It causes torsional irregularity. There is a distance of about 5m between the centers of mass and stiffness. .Most of your columns are operating above 1% in percentage and this shows that they are struggling as a moment. In the same way, some of your columns have fallen into weak colon status. It would be beneficial to increase the sections. .In a structure with such a number of floors as the narrow side of the column, min. I recommend using 30cm. In addition, in this case, your stirrup spacing increases to 10 cm in the column tightening area and there is no problem in the application. .If there is no problem in terms of architecture, adding symmetrical curtains in both directions (converting some columns to curtains) while keeping your existing curtains will relieve the system. .I can't say it's completely wrong from the column to the console design. As a result, effects and deformations are calculated according to this design in the 3D analysis system. The ideStatik team states that there is no difference in terms of analysis when modeling beams such as .K31 as one or two beams. As a result, the program creates a nodal point at the point where the stud comes and divides the beam into two. Only the reinforcement design will be different. If we slurred, be forgiven...