Hello, I am getting a stapling error on some curtains on the 1st Basement Floor in my project. I couldn't figure it out no matter what I did. I also increased the slab thickness, but min. I need 25 cm flooring. I want to solve this method without doing it as much as possible. I wonder why it doesn't give the same error on other floors. Thank you from now. Project:
You do not have permission to view link Log in or register now.
 
Hi, Stapling control is required in cases where the curtains have floor connection without beams. In the current situation of the project, the punching design stresses in the parts connected to the flooring in the P13-14-24-25 numbered curtains in the basement floor exceed the limit value (concrete tensile strength) but do not exceed it in the other floors. You can cancel the stapling control by inserting beams at the ends of the relevant curtains in the basement. In the project; -P3-P16, P4-P21-P31, P15-P9, P10-P22 curtains should be defined separately as group curtains.
You do not have permission to view link Log in or register now.
-We recommend analysis according to the semi-rigid diaphragm method in the project. -For a precise calculation, we recommend you to reduce the width of the slab, curtain and raft finite element. (For example 25 cm) Good work.
 
Since I got a stapling error in the raft slab, I solved the problem by adding the stapling reinforcement with closed stirrup strips to some columns, but I can't get the stapling reinforcements in the drawings. I think it should appear in the basic application plan. Do I have to draw? If so, how should sample drawing be made?
 