Cork flooring analysis

aykutkeskin12

New Member
Hello, after analyzing the project I am working on, it gives an error no matter how much I increase the floor thickness. Do I need to design it differently in cork flooring? -We are told to give the thickness of the column headings and the height of the table 0 in the forum, but how is it in practice, is it not done at all?
 
Re: CORK FLOOR ANALYSIS Hello, You used 20cm thickness for cork flooring in the project you sent, which seems sufficient. There is no error with the thickness. There is no problem in the main reinforcements on the floors, only inadequacy in the additional reinforcements. In the Concrete Slab dialog, enter the additions tab. You can increase the diameter of the additional reinforcement you use for slabs or reduce their spacing and change the Existing AS to meet the AS required. 0 thickness placement of column heads is required for slab punching checks in reports. There is no situation affecting the application. Perform analysis by selecting semi-rigid diaphragm and Use earthquake effects in floors in cork flooring analysis. I recommend you to review this topic as well.