It is normal for the period to decrease when you add curtains to the structure. Because you increase system rigidity. If you add the two projects without curtains with curtains, which you conclude that there is a "very big drop" in periods when you add curtains at 7, we can look at it. It is not a situation that we know and observe that there is an "incredible period" difference for the structure where all data entries are the same between 7 and 8. Solve the same structure in 7 and 8 and you'll see similar results. If you add the two projects that you don't see the "amazing period" difference, we can take a look. As a data entry, you must confirm that the two projects are the same. 8, there may be a difference in the reinforcement area consisting of tensile axial force, if any, in the column reinforced concrete design. This is a possibility we added in 8. However, the reinforcement area, which can be formed by column tension and axial force, does not cause "incredible column price difference". If you add the project that you observed to be out, we can take a look. According to TBDY 2018, the periods are different from the periods observed according to TBDY 2007, due to the use of element-effective stiffnesses in the solution. Your last message has nothing to do with your first column beam shear safety question. I have stated in my previous message on which aspects the column beam shear safety control depends.