BODY REINFORCEMENT FOR BEAMERS LARGER than 60 CM

oguz atalay

New Member
Hello, in the regulation, there is a requirement to add body reinforcement to beams higher than 60 cm, but in the project I have presented in the appendix, the program did not add body reinforcement to beams of 70 cm. I don't understand, is there something I entered wrong?
 
Hello, the beams you call beams higher than 60 cm are seen as cantilever beams in the project. Cantilever beams are exempted from body reinforcement requirements as they are not considered as frame members. If you want to edit the web reinforcement for these beams, you can enter the web reinforcement in the beam reinforced concrete dialog. Good work
 
hello sir. Is there any information in the regulation that the body reinforcement should be thrown in the frame beams and not in the cantilever beams? I could not find it and it is difficult to explain during the control phase.
 
thank you sir. ahmet, it was mentioned in TDY article 3.4.2.5, I must have overlooked the article, I had manually thrown the body reinforcements in my previous projects.
 
"For beams with a body height greater than 600 mm, there shall be at least the amount of body reinforcement determined by Equation 7.6." This expression is included in the TS500.
 