In this type of flooring, you should check the reinforced concrete calculation axles. The program defines automatic reinforced concrete calculation axis type depending on the structure of the flooring. Although it should not be console flooring, it acts as console flooring. Or the reinforcement type can be flat piye or otherwise. However, what you want is the beamless floor reinforcement type. In this case, it makes a thickness query as a program depending on the reinforcement type. Then you get a warning of insufficient thickness. For example, in your project, the calculation axis no. 8 on the D174 floor in the 1st basement was intended to be operated from the P37 curtain as if it were a console. At that time, the program considers the 19.25 m console as a slab, and therefore finds the thickness insufficient. What needs to be done: With the reinforced concrete calculation axis edit command 1- Decide how the slab works and edit it accordingly 2- Write the required clearance value for thickness control and tick the box. Check this out for other account axes as well. Choose flat reinforcement at the bottom and the top. N. YILMAZ