Basically Fixed Load Identification (Question)

gokhanseker

New Member
Since there is basically a fixed load subfloor, the load totals shown in the fixed load calculations and on the foundation (doesn't it have to be 1.96t/m2?) are different. What is the reason for this?
 
"gokhanseker":3hrgn6o3" said:
Since basically there is a constant load subfloor, the load totals shown on the fixed load calculations and on the foundation are different (1.96t/m2 isn't it?) What is the reason for this?
Floor self weight is added automatically. You can see the total value DisplayValue=SlabThickness*ConcreteUnitVolumeWeight+PaymentLoad DisplayValue= 0.73*2.5 + 1.61 = 3.435 tf/m2
 