B1 disorder

Hi My suggestions --1. Remove the basement ticks of the curtains in the basement, -- Brace the stairs, Ünver ÖZCAN
 
Thank you for your answer, Unver. When I remove the flood tic, the problem is solved, this does not give an incorrect result in terms of calculation, right?
"unver":1kzjnqmi" said:
Hello My Suggestions --1. Remove the flood tic of the curtains in the basement, --Support the stairs, Ünver ÖZCAN[/quote ]
 
"ernylmaz39":2bokwpp9" said:
Hi, I get B1 irregularity error when I define curtains as basement curtains in my project. I would appreciate your help. Thanks.
You do not have permission to view link Log in or register now.
Hello, There is no diaphragm formation on the Basement floor, except for the balcony slab on the Basement floor. Columns without slabs are not included in the floor effective shearing area in B1 irregularity control. You can define the column areas manually.Note: Since there is no diaphragm formation on the basement floor except for the D13 Balcony floor, it would be appropriate not to accept the floor as rigid (Rigid-X and Rigid-Y will not be marked for the basement floor in the General Floor Settings dialog). I suggest checking "Creating rigid diaphragm" option in the tab. In this case, since there is no diaphragm formation in the basement floor, for the sub-basement floor B1 irregularity check will not be performed. B1(You can review the document linked below about Weak Floor Irregularity.
You do not have permission to view link Log in or register now.
Note: The lower edges of the stairs on the ground floor are not supported by any element.
 