As far as I understand from your article, the building was designed and manufactured before. If I understood correctly, 1-this is the current building evaluation+new building project work. 2- If only the project has been done and no production has been made, it is necessary to re-project. this is the easy part. As in the 1st article, the conformity of the building elements in the situation a-place with the project is determined. If any, incompatibilities are reflected in the project. b- reinforcement is determined (especially stirrup tightening, stirrup hook detail, shoot length, tension reinforcement overlap length etc.). the current situation is reflected in accordance with the program. c-concrete is determined. At least 3 cores are taken on each floor and not less than 9 in total in the building (intermediate knowledge level). the mean-standard deviation of the cores is found. For the cylinder transformation, the concrete fcd value is obtained by multiplying the value of 0.85. d-A computer model of the system detected in place is created. The e-top floor carrier system is also created. Before the f-structure analysis, the column-beam-wall reinforcements of the existing floors are fixed. g-structure analysis is done. Regulation checks are made regarding the newly added parts. newly added floors must comply with the regulation. h-linear performance analysis is done. If there is no brittle element in the structure and it provides life safety performance (for housing, etc.), the process is completed. I- If there is a brittle and collapsed element, it is strengthened. general structure translations are also checked. In structures with more than 3 floors, only element-based reinforcement is not allowed. j-As a recommendation, check the foundation stresses...