"HakanŞahin":fynzskgc" said:
In your opinion, for which reinforcements of the building elements used in the program are the reinforcements described in position 1? For example, in columns and panels, the shoots are clamped with 1.5lb. Beam mounting fixtures extend to 1/4 of adjacent span, always greater than 1.4lb. Which reinforcements do you think do not enter this condition?
It says that Lb length from the equation given in TSE500 9.1.2.1 should be increased by 1.4 for the bars entering position 1. Again in TSE500, it says L0 = a1 * Lb in the 9.2.5.1 overlay appendix. When we take a1 = 1 here, it turns out L0=lb. Again, the same article says that the overlap length is increased by 1.4 for the bars that enter position 1 for L0 length. Now, for example, we have a raft slab with C30 concrete. For the upper reinforcement (Position 1), the lb length we calculated in equation 9.1 at the beginning turns out to be 35Ø. Since the position is a reinforcement according to the rule in 9.1.2.1, we increase this length by 1.4 and make 35*1.4 = 50Ø. This is our clamping size. When calculating the raft upper floor overlap length, according to the equation in 9.2.5.1, L0 = a1* Lb here becomes L0 = 1 * 50 = 50Ø. However, the same article says to increase this overlap length by 1.4 for a positioned rod. That is, for position 1, L0 = 50*1.4 = 70Ø. This is greater than the Lb*1.5 we get in the program.